admin 管理员

有 58 人收听 TA

安规仪器网www.ag17.wang 安规商城www.17-18.cn

2146主题 2305回复 121859积分
发新帖

[电线燃烧] 电线电缆垂直托架火焰测试Vertical-Tray Flame Tests: IEEE 1202, IEEE 383, and U...

[提交至百度]
时间:2019-2-7 10:58 0 634 | 复制链接 |

1分钟快速注册,QQ|微信|百度|360帐号可登录

您需要 登录 才可以下载或查看,没有帐号?立即注册 qh360_login 

x
Vertical-Tray Flame Tests: IEEE 1202, IEEE 383, and UL 1685What Are Vertical-Tray Flame Tests?
Vertical-tray flame tests are commonly used in the wire and cable industry to analyze cable flame propagation for industrial control and power cables. These tests specifically examine the flame spread on cables installed in a vertical test chamber, simulating real-world industrial cable conditions when installed in a cable tray or other support systems.
Standard cable flame-propagation tests benefit cable manufacturers, electrical distributors and end-users. These procedures provide consistent, repeatable results and measurable test acceptance criteria that allow the selection of the correct product for the application. The standard flame tests commonly specified in the industry are UL 1685, IEEE 1202, and IEEE 383.

Overview of the UL 1685 Standard
UL 1685 Vertical-Tray Fire-Propagation and Smoke-Release Test for Electrical and Optical-Fiber Cables is an industry standard that provides the test methods for two types of vertical flame tests:

  • UL Flame Exposure
  • FT4/IEEE 1202 Type of Flame Exposure
The UL version and the FT4/IEEE 1202 version both measure flame propagation by testing groups of cables. These tests vary in the cable loading, spacing, burner angle, flame spread and optional smoke requirements. UL cable standards provided in Table 1 allow control and industrial cables to meet one of the UL 1685 vertical flame tests to be UL listed.

Cable Standard
Cable Types
UL 13 Power Limited Cables
PLTC, CL3, CL2
UL 1072 Medium-Voltage Cables
Type MV-90, MV-105
UL 1277 Tray Cables
Type TC
UL 1569 Metal-Clad Cables
Type MC

Table 1: UL Control and Instrumentation Cable Standards Containing Vertical Flame Tests

The UL Flame Exposure test of UL 1685 measures the flame spread in groups of cables in a steel ladder tray. The tray is 12 inches wide, 3 inches deep and 96 inches long. The rungs measure 1 inch in the direction parallel to the length of the tray and are spaced 9 inches apart. The tray is mounted vertically on the floor of the test chamber or on an optional tray base and the center of the tray is filled with cable samples in one layer spaced 1/2 cable diameter apart. A mixture of air and propane is burned using a ribbon burner. The burner is placed horizontally 3 inches from the surface of the cable, 18 inches from the bottom of the tray and midway between two rungs. The power output of the burner is 70,000 Btu/hr. The flame is applied for twenty minutes and then removed.
A cable passes the vertical-tray test if the cable char height is less than 8 feet. A cable may continue to burn after the burner is shut off; however, the test is not complete until the cable stops burning. The UL Flame Exposure test also contains an optional smoke test. Cables that meet the smoke test have to meet the following requirements:
a) The total smoke released is to be 95 m2 or less
b) The peak smoke release rate is to be 0.25 m2/s or less.

1471900830403.jpg
Figure 1: UL Flame Exposure Test Chamber
1471900830400.jpg
Figure 2: FT4/IEEE 1202 Test Chamber Test Chamber


UL 1685—FT4/IEEE 1202
The FT4/IEEE 1202 Flame Exposure version of UL 1685 is similar to the UL Flame Exposure version but contains a few variations. This test measures the flame spread in groups of cables in a steel ladder tray. The tray is 12 inches wide, 3 inches deep and 96 inches long. The rungs measure 1 inch in the direction parallel to the length of the tray and are spaced 9 inches apart. The tray is mounted vertically on the floor of the test chamber or on an optional tray base. The tray is filled with cable samples. Depending on the outer diameter of the cable, different spacing requirements apply. A mixture of air and propane is burned using a ribbon burner. The burner is placed at a 20° angle 3 inches from the surface of the tray, 12 inches from the bottom of the tray. The power output of the burner is 70,000 Btu/hr. The flame is applied for twenty minutes and then removed.

A cable passes the vertical tray test if the cable char height is less than 4 feet, 11 inches. A cable may continue to burn after the burner is shut off; however, the test is not complete until the cable stops burning. The FT4/IEEE 1202 also contains an optional smoke test. Cables that meet the smoke test have to meet the following requirements:

a) The total smoke released is to be 150 m2 or less
b) The peak smoke release rate is to be 0.40 m2/s or less

IEEE 383 Flame Test Reference
IEEE 383 is a Class 1E Nuclear Standard and provides requirements for cables and installations used in nuclear power generation facilities. IEEE 383 previously contained a flame test in the 1974 version but was updated in 2003 and again in 2015. In 2003, the flame-test procedure was removed from the standard. Instead, IEEE 383-2003 Section 8 points users to IEEE 1202 as shown below: Cables shall be flame retardant in accordance with the requirements of IEEE Std 1202-1991 or NFPA 262-2002. Switchboard cables, coaxial, twinaxial, and triaxial cables shall as a minimum pass the UL VW-1 flame test.* Many existing cable specifications reference IEEE 383 in the cable flame-performance section for historical reasons. Based on the above reference, cables that meets the IEEE 1202 flame test meet the flame-requirements of IEEE 383.
*Source: IEEE 383-2003 Section 8
您需要登录后才可以回帖 登录 | 立即注册 qh360_login 

本版积分规则

关闭

快领红包上一条 /2 下一条

多功能温升仪 线束电压降仪 连接器温升仪 端子循环电流 大电流温升仪 燃烧测温铜块 UL94燃烧仪 电线燃烧仪 印度燃烧仪 低温卷绕箱 低温拉伸仪 透明水槽 滚桶跌落 耦合器侧拉
美华认证网|安规网|安规标准|美华安规X

高精度功能强大的UL94燃烧测试方案

优 化 版:在UL实验室方案优化而成/UL94标准全功能/功能强大测试软件/丰富灵活的测试夹具及操作体验/0.8立方较大空间/高精度流量计/50W/超过国内很多国家级/省级/民营第三方/研究所所用同类型产品。 特色优点:给UL及UL美华实验室、多家知名实验室及全球知名塑料公司规划及开发UL94燃烧箱之工程师团队自研,外形全新设计;结合UL工程师经验和美华人机合一理念及高操作性要求,软件强大全面;价格美丽动人;不少设计和理念远超同行。...

点击查看详情 
快速回复 返回列表 返回顶部